Online assistance for electrical trade people Login  |  Register  |   Forgot Password
Assistance for electrical trade people
 

 

 

 


Click here to send Ron a pdf document for publication on this Topic

Documents must be less than 200k in pdf format

Posted By Topic: Ev Chargers

WillJ
Sep 08 2017 08:43

Hi All

Apart from the info on the engerysafe website, is there anything else i can look at regarding charger installations? particularly public charging

Got a couple to install next week and want to make sure we get everything ok

Thanks
   

pluto
Sep 08 2017 09:55

The manufacturers instructions and any additional information from the NZupplier.
   

JonoQC
Sep 08 2017 15:35

Nothing specific that I've seen, but in my case I installed a separate RCD just for the vehicle charger (peace of mind that the car will still charge overnight even if something else trips). There's also some logic to recommending running larger cable than the minimum for voltage drop as it will save some loss.

16A charger on 2.5mm is around 3.4W per meter where 6mm is 1.4W/m. Average EV spends around 400-600 hours charging a year.
   

WillJ
Sep 08 2017 16:11

Thanks, we are doing a couple of Tesla Chargers. they have a fairly decent current draw depended on how fast you set the charge rate too

We are running 3phase 16mm for ours
   

JonoQC
Sep 08 2017 17:45

Ah, right. The Tesla wall chargers are a lot better than most, given the level of adjustability. Different kettle of fish in terms of power level, as well!
   

WillJ
Sep 20 2017 20:32

Does anyone know the reason for Type B Rcds for Ev chargers, the ones for our job are about 500 from Schneider (4p)


   

ppaw1965
Sep 20 2017 20:58

Will most likely be because of nuisance tripping you would get otherwise. I know of at least 1 brand of VFD that requires this. And yes until more widely used extremely expensive.
   

pluto
Sep 20 2017 22:08

the reason for type B RCD is because of the continuous and constant DC residual currebts in the supply connection if greater than 6 mA current TYPE B is required.

BTW the Worksafe guidelines for EV charges mandates the use of type B RCDs for large EV chargers due the DC rsidual current levels (pulstaing and constant) under earth fault conditions.
   

WillJ
Sep 21 2017 07:52

Yer i thought the Dc factor was the reason
We had advice from the manufacturer of the charger that NZ work safe guideline were very extreme and that elsewhere in the world they all use type A RCDs
   

pluto
Sep 21 2017 09:02

WillJ Sep 21 2017 07:52
Your comment (part only)

We had advice from the manufacturer of the charger that NZ work safe guideline were very extreme and that elsewhere in the world they all use type A RCDs

My comment

That is incorrect, the WorkSafe NZ EV rules follow the international standard IEC 61851 series in the choice of RCD type.

   

AlecK
Sep 21 2017 09:17

Just to be clear, it's not about "nuisance tripping", but instead it's about avoiding failure-to-trip under fault conditions.