mowgli
Mar 26 2018 12:41

In a single phase PEC submain comprised of three cores plus screen ... with red=phase, white=PEC(GY), and screen=neutral ... is there any advantage sleaving the blue to black as a neutral conductor? Will removing the flow of current in the screen result in a cooler cable?
   

DougP
Mar 26 2018 13:01

I would be using the screen as earth, and sleeve the blue as neutral.
As originally intended for 3ph use, the screen would have been earth in any case.
   

mowgli
Mar 26 2018 14:06

Thanks DougP. I guess I was overthinking the application of NS