Posted By Topic: Gas meter

Tommy
May 07 2018 16:02

Hi how close can a heat pump and heat pump isolater be to the gas meter on domestic house
Thanks
   

pluto
May 07 2018 16:44

Use figure 4.11 of as/nzs 3000, the shaded areas are the "no go" zones with no electrics permitted, unless it is assoicated with the gas meter.
   

Tommy
May 07 2018 17:04

I have only got asnz 3000 2007 can’t find it in there is it 1 meter to the side of gas meter to heat pump or is it 1.5 meters thanks
   

Ristov
May 07 2018 17:19

The figure is under 4.18.3 - 800mm radius from the gas pipe.


   

Sarmajor
May 07 2018 19:41

Tommy, if you are a sparky you can download AS/NZS3000:2007 for free by logging onto the EWRB web site and using the link to Standards NZ.

   

AlecK
May 08 2018 08:22

Just remember that the words of that clause are changed by the citation of "3000" in Schedule 2 of ESRs.