Posted By Topic: Adding power points in kindergarten

MK1AVO
Nov 19 2018 08:42

Hi all, i have a kindergarten with no RCD protection whatsoever.
I have been requested to add a power point in the kids play area for a fridge there is a local power circuit close by which is also feeding a couple of outlets in the kitchen and the play area.
Can i add a 10mA outlet for a fridge and advise them they have no other RCD protection?
What are my obligations?
   

AlecK
Nov 19 2018 10:46

Obligation under ESRs:

"in a kids' play area" would be an area "primarily for purpose of teaching or caring for children", so as per 2.6.3.2.2(a) [2007 +A1+A2] the new socket must have 10 mA RCD protection unless an exception applies.

Could go further, and apply 2.6.3.3.2 [2018]; which would mean 30 mA for new subcircuit & 10 mA for new socket; again unless an Exception applies. Or, if adding to an existing subcircuit, 30 mA at origin of new cabling & 10 mA at socket.

Obligation as electrical professional:
Advise you client of current rules; and relevance of RCDs to HSW requirements.
Also check whether, as a kindergarten, any Min Ed rules apply.


   

MK1AVO
Nov 19 2018 15:20

Thanks Alec, its just becoming a mine field out there these days with interpretations.

   

OwenK
Nov 19 2018 22:12

http://www.education.govt.nz/assets/Documents/School/SchoolsBulletin/Issue27HUP7ElectricalInstallationStandards.pdf

74 pages of bedtime reading to put you to sleep