murphyJ
Dec 13 2018 20:29

Have been asked to carry out COPV for small extension with about 4 power points looped off existing part off house. The extension was done in 2001, just wondering if anyone knows when RCDs where made mandatory for extension of a power point circuit
   

DougP
Dec 13 2018 21:20

RCDs weren't required for extending an existing non-RCD protected circuit until the 3000:2007 version.

Additions were specifically excluded in 3000:2000 version.
   

murphyJ
Dec 13 2018 21:37

Thanks for that