Installed new LED lights on a C16A MCB. The load is 10.5A when the lights are on. But randomly the MCB is tripping. We have done insulation test and RZ loop test but can't find any faults. Anyone else had the same issues with LED lights?
   

medistat
Nov 12 2019 09:09

How many/what size LEDs are sucking 10.5A (2300W+)?

Does it only pop at turn on or during running?
   

DougP
Nov 12 2019 10:14

You mean an RCBO?
Possibly tripping on inrush current, not leakage.

I'm guessing you're talking about big highbays or something?
   

Someone
Nov 12 2019 20:09

I'd be blaming inrush.

Consider a D16 or C20 if you have enough loop impedance available, split the circuit, or use different fittings.